Hi Guys,

In my home theater that's underway, I was planning to do a flush mount equipment rack similar to what member "YW84U" did, with the equipment housed in its own room off to the side.

The volume of this equipment "closet" is approximately 79 cubic feet.

What do you recommend for a ventilation fan? I'm thinking I should definitely provide something so I can prevent that interior space behind the equipment from getting too hot.

I'm not completely sure on the exhaust routing but I think I can send the fan outlet out above the adjacent bedroom's closet and out to an exterior foundation wall of the house.

I'm not even sure how I should spec a fan for such a small room. Only that I should probably get one that is quiet.

Any ideas would be appreciated. Thanks.
 

·
Registered
Joined
·
451 Posts
Discussion Starter · #3 ·
How did you go about sizing it?

I just did the rule of thumb calc which takes floor area x 1.1 (for 8ft ceiling) to determine CFMs.

Based on my equipment room size, which has a floor area of 4.125 ft x 3.08 ft, that works out to ~14 CFMs. (Based on 8 air changes per hour, which is at least the ventilation requirement for bathrooms).

However, the ceiling height in this equipment room is less, closer to 6ft. (6.25 ft). So even 14 CFMs might be too high, depending on what the criteria should be.

If the numbers above are anything to go by, the required fan might be quite small.
 

·
Registered
Joined
·
451 Posts
Discussion Starter · #4 ·
I'm thinking I need a different criteria. 8 air changes per hour is probably based on moisture control for a bathroom and has nothing to do with heat removal.
 