If you have a natural draft water heater or furnace, pulling out 680 cfm may cause carbon monoxide poisoning.

For that amount of air, a 8-10"+ pipe may be required; chances are that there isn't enough clearance for that. Most install manuals spec out the pipe size required and the maximum equivalent length.